I think a problem here is that guidance, and 'guidance lists', seem to be thinking of 'polarity' in a somewhat restricted sense. In relation to pre-energisation 'polarity' testing, 2.7.11 of GN3 says:Yes, it is an 'expected' test and should normally be done. I'll give you a clue........it's the 4th test on most guidance lists and goes by the name of 'polarity'. Perhaps you would be so kind as to tell us how you would confirm 'polarity' on a 'radial' socket circuit, by testing, during 'initial verification' - without using the method I described or a wander lead??If one followed that guidance, one would, indeed, pick up L-N reversals and even N-E reversals, but a circuit with an L-E reversal, such as the fatal one we've been discussing in this thread would, presumably pass such a test with flying colours - after all (R2+R1) is the same as (R1+R2)."For radial circuits, the (R1+R2) measurements, made as in test method 1 (Section 2.7.5), should be made at each point"
Kind Regards, John.
No, no, no...... 'polarity' is the confirmation that single-pole accesories/devices are wired in the 'line' conductor only (put simply).
So, answer my question - How do you confirm 'polarity' on a 'radial' socket circuit, by testing, during 'initial verification' - without using the method I described or a wander lead???
And when you can't answer, will you then please concede - for others who are reading - that the method I described, or the wander lead method, are 'required' tests.
You see, the whole point of this......if we're going to speculate about the OP.......is that had 'polarity', of the socket outlet in question, been confirmed in the correct manner, the tragic accident may not have happened...........but some people (including qualified sparks), are under the impression that 'flicking' the socket switch during the R1 + R2 test confirms 'polarity'....IT DOESN'T........that only applies to lighting radials!