Need to run two sockets outside and plan on using 2.5mm SWA T+E. One socket will be 6 metres from the house, with the second socket being a further 20m away. I plan to use a radial circuit. Will this be OK in terms of volt drop, safety, etc.
Just want to check guys before I install it at the weekend.
BTW, the cable will be supplied from its own RCD on the consumer unit.
Cheers