coax and power cables running together?

Joined
17 Aug 2004
Messages
375
Reaction score
3
Country
United Kingdom
Is there a certain distance i should keep standard coax & rg59 cable from a 240V (13Amp) cable? or will it not inerfear with the signal?


I have a few coax & 13Amp cabling running together (previous owner) - should i seperate them?

Thanks
 
Sponsored Links
Regulation 528-01-04
50mm separation between Low Voltage (50v - 600v) and telecomms cables (this includes IT netwoking cables).
 
Thanks, i had a feeling they should be seperated, 50mm is not to bad though.

Whata bout 2 coax cables, ones got a 5v - sky digi link, should i ideal seperate these aswell?


Cheers
 
Sponsored Links
50mm separation need not be maintained, provided that:
(i) the LV cables are enclosed in separate conduit which if metallic is earthed in accordance with BS7671, or
(ii) the LV cables are enclosed in separate trunking which if metallic is earthed in accordance with BS7671, or
(iii) the LV cable is of the mineral insulated type or is of earthed armoured construction.
 