I am looking to split the ring in my flat to install some additional sockets whilst installing thermal & acoustic insulation. My intention is to run new 2.5mm T&E cabling directly clipped to the existing, plastered brick wall horizontally from the existing socket to the new location. The wall will then be insulated with 50mm of acoustic insulant and boarded out.
Am I correct in my interpretation of the reference methods that method 100 applies ? And that from table 4D5 that the current carrying capacity of each cable will be 21A and thus that this is an acceptable installation ?