Creda Electric Shower = Low Pressure

Discussion in 'Electrics UK' started by cardiffdutch, 12 Feb 2007.

  1. cardiffdutch

    Joined:
    12 Feb 2007
    Messages:
    6
    Thanks Received:
    0
    Country:
    United Kingdom
    I replaced an old essential shower in my house for a Creda 550c 9.5kw shower. After I installed I wasn't happy with the force of the shower so I changed it for the 10.4kw version and it improved slightly but not much. Both of these new units are way less powerful than these new units. I don't get a low pressure warning either. When the flow is cold it is very powerful but as soon as you increase the temp it is pathetic.

    Any ideas??
     
  2. securespark

    Joined:
    11 Jan 2004
    Messages:
    25,997
    Thanks Received:
    501
    Location:
    Cheshire
    Country:
    United Kingdom
    First of all, what is supplying the shower?

    What size cable, switch, mcb, rcd, CU, and is there any bonding?
     
  3. cardiffdutch

    Joined:
    12 Feb 2007
    Messages:
    6
    Thanks Received:
    0
    Country:
    United Kingdom
    The cable is 10mm shower cable. I had to cut the old cable and connect another piece to it as the old cable wasn't long enough. I connected the cable by using a junction box (i think thats what its called). Im not sure what the other things are you are asking.

    Thanks for the response.
     
  4. davy_owen_88

    Joined:
    17 Nov 2006
    Messages:
    1,680
    Thanks Received:
    2
    Location:
    West Glamorgan
    Country:
    United Kingdom
    I hope it was a 60A junction box...
     
  5. cardiffdutch

    Joined:
    12 Feb 2007
    Messages:
    6
    Thanks Received:
    0
    Country:
    United Kingdom
    I think it was - Exceuse my ignorance but would that affect the showers performance. I presume there is a risk of blowing the shower and tripping the house if it isnt a 60amp junction box.
     
  6. bernardgreen

    Joined:
    3 Nov 2006
    Messages:
    12,344
    Thanks Received:
    1,042
    Location:
    Bedfordshire
    Country:
    United Kingdom

    Overheated junction boxes toast themselfs and turn into carbon which conducts electricity where it should not be going..
     
  7. cardiffdutch

    Joined:
    12 Feb 2007
    Messages:
    6
    Thanks Received:
    0
    Country:
    United Kingdom
    I will double check tonight - Have you got any ideas of what could be causing the poor performance. I am thinking of chnging it for a Mira shower as I have heard that give the best performance.
     
  8. securespark

    Joined:
    11 Jan 2004
    Messages:
    25,997
    Thanks Received:
    501
    Location:
    Cheshire
    Country:
    United Kingdom
    If your JB is round, you have installed an entirely inadequate one. AFAICT, you can't get round 60A JB's.

    There should be no unneccesary joints in a cable like this.

    What about the rest of the circuit?

    Switch size, MCB size, RCD present, which CU have you got, bonding etc, etc..
     
  9. Steve

    Joined:
    15 Apr 2005
    Messages:
    16,009
    Thanks Received:
    226
    Location:
    Yorkshire
    Country:
    United Kingdom
    To add, you NEED to know ALL of these particulars BEFORE you make any change to a shower circuit. Without knowing these, you could be making a totally dangerous situation by fitting a higher powered shower or making other modifications.

    Also note that modifications to fixed wiring in a bathroom is notifiable to your local building control under part p of the building regulations. You are breaking the law by doing this work and not notifying.

    Please get an electrician in to ascertain the safety of your shower circuit.
     
  10. ricicle

    Joined:
    14 Sep 2006
    Messages:
    6,347
    Thanks Received:
    383
    Location:
    Gloucestershire
    Country:
    United Kingdom
    I agree - and do not use it again until you have!!
     