Hi Guys I was wondering if anyone has any suggestions on my fuse box problem Ive just noticed :- my kit is
a 10w CU with 63A RCD split and 100A DP switch
I have 6 MCBs all on the non RCD side .. ? before I moved in..
which are
6A - upst lights
6A - Dn lights
16A - Shed pwr,imersion heater
32A Upstairs Ring
32A Dnstairs Ring
50A cooker
the problem is the dnstairs 32A its getting hot to the touch at certain times ie kettle on, baby steriliser but cools fast once these things go off - takin the lid off I see 2 lives going to the the MCB one has about 1/2" of damaged/melted insulation so something is wrong .. the MCB has never tripped out either any suggestions before I get a sparky in ?
Paul
a 10w CU with 63A RCD split and 100A DP switch
I have 6 MCBs all on the non RCD side .. ? before I moved in..
which are
6A - upst lights
6A - Dn lights
16A - Shed pwr,imersion heater
32A Upstairs Ring
32A Dnstairs Ring
50A cooker
the problem is the dnstairs 32A its getting hot to the touch at certain times ie kettle on, baby steriliser but cools fast once these things go off - takin the lid off I see 2 lives going to the the MCB one has about 1/2" of damaged/melted insulation so something is wrong .. the MCB has never tripped out either any suggestions before I get a sparky in ?