plugwash said:
i seem to remember the stuff you posted from mk said they had tested theier sockets to 19A continuous without any damage.
I knew I used to have this, but I thought I'd lost it. I was right and wrong - I do still have it.
From
BS 1363:1984 Incorporating Amendment Nos. 1, 2, 3, 4, 5 and 6
Specification for 13 A fused plugs and switched and unswitched socket-outlets
16 Temperature rise
16.1 Accessories and their surroundings shall not
attain excessive temperatures in normal use.
16.1.1 Compliance shall be checked by the tests
described in 16.1.2, 16.1.3 and 16.1.4 for plugs,
fixed socket-outlets and portable socket-outlets
respectively.
The tests shall be carried out at rated voltage.
16.1.3 describes in painful detail how sockets are to be mounted and supplied. They are then asked to pass a current through a special test plug, and with single sockets there is an additional load on the supply cable.
The test currents are:
[code:1]Type of Plugs with Balance Total load on
socket connected loads of load supply cable
Single 1 x 14 A 6A 20A
Twin 1 x 14 A + 1 x 6 A 20A
Multiple
(fused) 1 x 14 A + 1 x 6 A 20A
Multiple
(unfused) 2 x 14 A 28A[/code:1]
The test is done in a sealed chamber, and run for at least 4 hours and at most 8, or until the temperature stabilises. Nothing must rise in temperature by more than 50°, and after the test, "the socket-outlet shall be in a serviceable condition".