desperate baxi solo 3

Joined
25 Nov 2005
Messages
93
Reaction score
0
Location
Liverpool
Country
United Kingdom
Please anyone out there with any help changed pcb board just getting ignition clicking as though no gas, worked for 3mins then just clicking again could it be solenoid thanks.
 
Sponsored Links
shaka said:
Please anyone out there with any help changed pcb board just getting ignition clicking as though no gas, worked for 3mins then just clicking again could it be solenoid thanks.


Why have you changed the pcb?

Was it doing the same before you changed the board?

Have you checked the pilot injector?
 
changed board as relays had burnt out,this has only happend since new board gone in, boiler ignited for about 5mins then went out then just started to click no overheating light on just no ignition.
 
Sponsored Links
I will invest in pilot injector, could you tell me why this has happened after replacing new pcb board,also solenoid sticking was another suggestion is this possible, thanks.
 