Hi guys...ive got a problem which is mostly covered by 1 of your FAQ's
but with maybe a tiny twist???
ive got a gloworm ultimate 60 bf.
a grundfos 3speed pump
a honeywell sundial y plan 3 position diverter valve
nine small rads.
plenty of hot water & stone cold rads...the systems been dodgy since we moved in this april..ie.turn the hot water only on.. & upstairs rads would get warm,not hot at same time
though at that time, the central heating did work both in conjunction with & independantly of hot water.
ive tried the manual overide on the zone valve which does induce the boiler to kick in & rads get hot but only when i hold the switch/lever right up to the top of the casing..the hook position is not far enough & i dont think it will stay on the hook even if it was high enough
what i need to know if possible & before i buy a new motor or whole valve is, is there anything else other than a broken motor that might cause these symptoms?
i hope this is enough info & thanks in advance
BTW fantastic forum
but with maybe a tiny twist???
ive got a gloworm ultimate 60 bf.
a grundfos 3speed pump
a honeywell sundial y plan 3 position diverter valve
nine small rads.
plenty of hot water & stone cold rads...the systems been dodgy since we moved in this april..ie.turn the hot water only on.. & upstairs rads would get warm,not hot at same time
though at that time, the central heating did work both in conjunction with & independantly of hot water.
ive tried the manual overide on the zone valve which does induce the boiler to kick in & rads get hot but only when i hold the switch/lever right up to the top of the casing..the hook position is not far enough & i dont think it will stay on the hook even if it was high enough
what i need to know if possible & before i buy a new motor or whole valve is, is there anything else other than a broken motor that might cause these symptoms?
i hope this is enough info & thanks in advance
BTW fantastic forum