Hi

My downstairs rads are ice cold and at the same time the upstairs ones are all heating fine. what could be the cause. please help.
 
Sponsored Links
Failing pump, sludge or not properly balanced!

Tony
 
Probably your Central heating pump. How old is it?
 
i got the house 3 yrs ago .the pump is a GRUNDFOS and have had no probs since

i have also checked all the rads for air and they are all ok,water trickles out. a friend advised me to drain the rads and when i did that there was black water coming out. the kitchen one started warming up. but when i closed the drain off and it cooled down,still not working.
put the pump on level three and can hear it buzzing
 
Sponsored Links
The flow from boiler will be very hot, the return pipe luke warm - a classic case of flow restriction. Either the pump has failed or there is a partial blockage - most likely a blockage. Usual treatment is to drain down, re-fil and add system cleaner and run it for a week. IF ok, drain and re-fil with clean water and add inhibitor.
If this dosn't fix it, the blockage needs more drastic action : powerflushing or undoing pipes to have a look - best left to the experts.
 
Use the bucket test on the D/S rads.

See FAQ on this site!

Tony
 
Hi guys i decided to change the pump, lo and behold still no heating :
 
Argile could'nt find bucket test in FAQ please let tell me how to go about the test.

cheers
 
I am not a pro, just an experienced DIYer.

You have already changed the pump and it didn't help. You have evidence of black in the radiators. I would get on with giving it a simple clean which will take a few hours of your time and cost you about £15. Very likely it will give you a cure, if not, it will do nothing but good in getting some of the sediment out, and will have cost you little.

Go into the loft, tie up the ball valve and bale out the mud from the F&E and sponge it clean (you don't want to add to the sediment load)

drain a couple of buckets of water out of the rad drain cock

Buy a litre of Sentinel X400 from any DIY shed or plumbers merchant for £15. Untie the ball valve and stir well to mix the cleaner with the incoming water so that it flows down to replace the water you drained out.

Run the system as normal for 4 weeks and it will loosen the sediment. You will know it is working when the circulating water goes inky black.

In the first few days, turn up the pump to fast (watch the F&E to make sure it is not pumping over) and go round turning one or two of the rads full on at both ends while closing the others, to increase the flow through those few rads, then do the others a couple at a time in the same way, and so on, then set it back to normal but with all rads open. If you find any of the rads are cold, turn down or close the hot ones until the cold ones heat up so that you know the chemical cleaner is circulating through them

After 4 weeks, turn off the boiler and tie up the ball valve, and drain out all the water with its loosened sediment, and refill/rinse/drain until it seems fairly clean. On final fill add a corrosion inhibitor such as Sentinel X100 for another £15, and balance the rads as shown in FAQs.

If you can do basic plumbing and can afford £100, add a Magnaclean. I guarantee you will be amazed and delighted by how much sediment it collects, and it continues working permanently to prevent black sediment collecting into a new blockage.
 
CHEERS GUYS I WILL START THIS WEEKEND AND LET YOU KNOW HOW IT GOES.