Would you tick (or cross) this box on a MWC if:
The loop was 49.9 Ohm.
The system was TT.
There was no earth rod.
There was an meb to the water & gas, providing the 49.9 Ohms reading.
Now, I would cross the box & say earth continuity was unsatisfactory, because, although the reading is within the 200 Ohms & the system was protected by an RCD, it is coming from the wrong place.
PS. This was installed by a "pro" spark a week ago. Give me strength...
Tick or cross?
Anyone?