earthing

Joined
28 Aug 2010
Messages
2
Reaction score
0
Location
Cheshire
Country
United Kingdom
hi all

i have a light in my bathroom ip65 and is on a rcd fused spur wich is located outside the bathroom and i have a shower wich is on its own rcd there is no more electrical items in the bathroom other than the light and shower
do i need any earthing in the bathroom other than the two pipes under the sink bonded ?


the main water pipe dose have a 10mm earth to it


thanks 4 your time
 
Sponsored Links
What your asking is know as supplementary bonding, not actually earthing but I think I know what you mean.

If you work to the BS 7671-2008 standards then there are certain criteria that if met can mean that you don't have to bond the copper pipes in your bathroom. These are outlined in the REgs at 701.415.2

If you don't have a copy then for the sake of a few pounds I would bond the bathroom if it were copper pipes.

I noted you also said that the water main was bonded, if you have gas in the house you should also bond that as well.
 