electric hob and double oven
14 Aug 2007
Is it acceptable to use a twin cooker outlet to run a ceramic electric hob, double oven and cooker hood.
The 45a switch will positioned next to the electric hob, the double oven is across the room in a tall oven housing, approx 3m away from the switch.
It's 6mm from the 45a switch to cooker outlet, 6mm again over to feed the double oven and 2.5mm feeding the cooker hood.
It depends
What is the rated consumption of the hob and the oven?
What is the value os the fuse/mcb protecting the circuit in question?
The spec of the oven is 0.79KW/H (5.7KW)
The spec of the hob is 6.3 KW.
The MCB is 32a
That is within the limits for the circuit. Assuming normal diversity rules.
I am concerned about your feed for the extractor fan, I would like to see that bit of 2.5mm going via an FCU on the way to the hood.
Use a dual appliance connector to connect up all your cables otherwise you will have 2x6mm + 1x2.5mm all in one junction.
Magic, thanks for that.
I could put the FCU in place of the unswitched socket at high level for the hood and hard wire.
You mean replace the socket for an FCU (ie not connected to the cooker circuit at all?)
My reading was that the hood is currently supplied by a 2.5mm² feed from the cooker circuit to an unswitched socket adjacent to the hood and that. following your suggestion, the OP, was asking whether he could simply replace that socket (still, presumably, connected to the cooker circuit) with an FCU.
Kind Regards, John
That's what I was meaning John.
Why not split the supply side ofthe cooker circuit and fit an isolator switch for each, one for oven and one for hob both local to its own appliance
If conditions permit you can upgrade mcb to 40A if required
Can you not supply hood from ring final circuit
Pulling it off the cooker circuit is poor practice imho
Do you think it's good practice to use a dedicated circuit to supply general various other appliances
It's not really 'various other appliances' - the cooker hood is part of the 'cooking set up'. Do you similarly feel that it is bad practice to run a gas hob's igniter from a cooker circuit?
... and how do you feel about cooker control units (fed from a cooker circuit) which include a 13A socket (presumably to be used for 'various other appliances')?