Electric Shower Prob

Status
Not open for further replies.
Joined
31 May 2005
Messages
2
Reaction score
0
Location
Ayrshire
Country
United Kingdom
I'\\\ve a 9.5Kw shower on a 45 amp circuit in a 100amp fuse box. The shower runs for about 1 min and then the fuse trips. It was working fine until the other day when the main fuse tripped when my misses was ironing. Changed the shower, then the fuse, then ran a 10mm cable from the fuse box direct to the shower ( just to make sure it wasn\\\'t the cable or the switch ). Did each independantly. Still trips after about 1 min. Anyone got any ideas what\\\'s wrong? I\\\'m due to move home in 10 days and in a panic!!
 
Sponsored Links
You would do better posting this on the electrics forum as obviously an electrical fault.

If you ask the Mod nicely he'll do it for you at no expense............ :D

MOD

we try to please ;)
 
what do you mean by the main fuse? fuses don't trip fuses blow and have to be replaced.

if nessacery post pics to show us exactly what tripped when

does anything seem to be running hot?
 
Sponsored Links
bd, need to know more info, is it an rcd main switch? try unplugging everything from socket outlets (unplug not just switch off) then try shower , if it hold plug things back one at a time
 
Thanks, for all the replies.
It was an iron for ironing clothes.
Yes I should have said RCD
My fault, didn't tighten up the neutral bar enough. Probably caused arcing and then the RCD tripped.

Where's the homer smiley when you need it ( doh !!! )
 
securespark said:
securespark said:
faulty iron?

Yes, Yes, Yes!! I was right, I was right, I was right!!!!!!!!
No, No, No!! You were wrong, you were wrong, you were wrong!!!!!!!!

bd2703 said:
Yes I should have said RCD
My fault, didn't tighten up the neutral bar enough.
Dodgy connection in the CU - nothing to do with the iron...
 
bd2703 said:
Thanks, for all the replies.
It was an iron for ironing clothes.
Yes I should have said RCD
My fault, didn't tighten up the neutral bar enough. Probably caused arcing and then the RCD tripped.

Where's the homer smiley when you need it ( doh !!! )

Try this one.

(Just funnin...
itsokay.gif
)
 
ban-all-sheds said:
securespark said:
securespark said:
faulty iron?

Yes, Yes, Yes!! I was right, I was right, I was right!!!!!!!!
No, No, No!! You were wrong, you were wrong, you were wrong!!!!!!!!

bd2703 said:
Yes I should have said RCD
My fault, didn't tighten up the neutral bar enough.
Dodgy connection in the CU - nothing to do with the iron...

:cry: :oops:

Feeling a bit of a wnaker...!
 
So changing the cable, switch and trip(or fuse) sorted it??

Umm.....

My bet it trips again soon :cool:
 
That wasn't what I meant, but perhaps we shouldn't go there..
________________________________
Moderator

post locked to prevent hi jacking
 

DIYnot Local

Staff member

If you need to find a tradesperson to get your job done, please try our local search below, or if you are doing it yourself you can find suppliers local to you.

Select the supplier or trade you require, enter your location to begin your search.


Are you a trade or supplier? You can create your listing free at DIYnot Local

 
Status
Not open for further replies.
Sponsored Links
Back
Top