I meant - as the person has done it, there was absolutely no point in installing a ring circuit in the garage.
It is not allowed to have more than one socket on a 2.5mm² spur cable without a Fused Connection Unit to limit the current.
When you have changed the spur cable to 4mm² cable it will be compliant and satisfactory.
Actually, I don't suppose the spur cable is 4mm² already is it?
Ah gotcha.
I'm going to check, but I highly doubt it as what I assume we're the original sockets were in there. They wires were relatively easy to fit into the new socket, can't imagine 4mm would be particularly easy