Given a 2.5kW wall mounted fan heater in a bathroom: does it go on a dedicated circuit or an FCU from power or lights circ? If on a FCU then what size fuse?
 
Sponsored Links
definalty not from lights

I would have thought fcu on ring, or dedicated circuit would be whats needed, 13amp fuse needed, best have it rcd protected, and watch the zones, thats if your are even allowed it in the bathroom to start with
 
tom - you need to put a bit of effort into learning some basic electrical theory. You really should have known, almost without having to think about it, that 2.5kW is over 10A, and therefore far too much for a lighting circuit.
 