flexicom 30hx

Joined
19 Dec 2010
Messages
1
Reaction score
0
Country
United Kingdom
I have a Gloworm Flexicon HX30 boiler.

Even though the set temperature is 80 Degrees the boiler fires and continues to run, but will only run at a constant 57 degrees, occasionally it will run up to 80 then it falls back to 57 after a few minutes.

The boiler does not switch off and does not lock out and does not show a fault code, but just runs at the low temperature.

The engineer has replaced the main PCB but that made no difference.

He came back and replaced the thermistors and that has made no difference.

The engineer didn't seem to have any other ideas,and he spoke to his senior engineer and he had no idea either!

Has anyone else had this fault or has anyone got any ideas why it does this?
 
Sponsored Links
poor circulation. Boiler is waiting for a rise in the return temperature, until it sees it it wont raise the flow. If you access D codes D40 and D41 you will prob see a temp differential of > 22c. There's nothing wrong with the boiler.
 
How warm does it get in the lounge after the heating has been on for several hours?
 