gledhill boiler

Joined
8 Apr 2006
Messages
7
Reaction score
0
Location
Norwich
Country
United Kingdom
we have a gledhill boiler mate 2 we have just had a plumber in who has told us that the pumps r not running and a possible fault with the time clock is there anyone who specialise in this particular boiler who can help please we live in norwich thanks
 
Sponsored Links
Sponsored Links
just-thinking said:
please tell us what was your original problem.[/quote ..........we have a real bad knocking and banging and gurling sound we have 2 turn the boiler off at nite coz its that loud ...we have enough hot water for shower but not bath and the rads r only luke warm
 
If I'm right you have three pumps on that system, one for the primary water, one for the CH, and the third for the DHW heat exchanger. On first impressions it sounds like the primary pump is not working properly so the boiler is overheating and banging, the heat store doesn't get up to full temp., and therefore the CH & DHW never do either.

Check the primary pump is operating (Boiler on, CH off, all DHW taps shut). Then check the small header tank (usually just above the Gledhill unit) is at least half full of water.
 