Planning a rewire for a 3 bed house with a High Integrity CU.
RCD1:
Upstairs ring
Kitchen ring (alternatively considering a couple of radials instead)
Downstairs Lights
Garage Lights
RCD2:
Downstairs ring
Upstairs Lights
Cooker
Garage ring
RCBO1
Alarm
No need for shower or immersion right now.
If I have hall/stairs/landing lighting with 2-way switching, is it best to put the hall and landing lights on the same circuit, so that only one circuit need to be isolated when working on a switch (for example)?
Having 2-gang switches controlling power on 2 circuits doesn't seem best.
RCD1:
Upstairs ring
Kitchen ring (alternatively considering a couple of radials instead)
Downstairs Lights
Garage Lights
RCD2:
Downstairs ring
Upstairs Lights
Cooker
Garage ring
RCBO1
Alarm
No need for shower or immersion right now.
If I have hall/stairs/landing lighting with 2-way switching, is it best to put the hall and landing lights on the same circuit, so that only one circuit need to be isolated when working on a switch (for example)?
Having 2-gang switches controlling power on 2 circuits doesn't seem best.