Halstead Best 50 boiler problem

Joined
4 Dec 2005
Messages
15
Reaction score
0
Location
Somerset
Country
United Kingdom
Hi Guys
My boiler has developed a fault which is puzzling me.
As from yesterday the boiler will ignite normally and run for 3 to 4 minutes and then close down. I can hear the pump still running and the HW thermostat is demanding 'heat'. All the radiators remain cold, the Thermostat is still demanding 'heat'.
The problem occurs both for HW/CH or just HW.
I might of suspected a problem with the 3 port valve, but the problem still exists if I manually open the valve using the small 'lever' on the valve head.
Any ideas would be appreciated.
Thanks for taking time to read about this problem.
Mahadev
 
Sponsored Links
Dear All
Quick update. I noticed when manually opening the valve the lever had not locked into the open position and had presumably closed. I reopened it and found the boiler ran normally.
So I guess it is the 3 port valve not working. See my post '3 Port Valve'.
It appears to be a fixed head, so what can I do to fix it?
To remove from the system I will have to cut 22mm pipework because of the way it has been mounted. Duh!

Has anyone successfully fixed a valve in place?
I believe one can get hold of a new motor and micro switches, but from where?
Thanks for your time
Mahadev
 