How much higher than the highest radiator does the expansion tank need to be in a pumped CH system? I'm thinking it only needs to be a foot or so but prefer not to guess. Anyone with advice?
Obviously the water level in the tank needs to be above the top of the highest radiator.
Installation Instructions say that the water level must be between 300mm and 30m (1ft to 100ft) above the flow connection of the boiler; which probably does not help a lot.
Pump manufacturers usually say that the level should be at least 1m above the pump inlet. Provided you meet all three criteria, you should be OK.
The boiler & pump is on the ground floor & the radiator in question will be on the 2nd floor (loft room) so I just need to move the expansion tank to be higher up the loft room wall than the radiator...but on opposite sides of the wall
The boiler & pump is on the ground floor & the radiator in question will be on the 2nd floor (loft room) so I just need to move the expansion tank to be higher up the loft room wall than the radiator...but on opposite sides of the wall