neilyp said:baxpoti said:neilyp said:I have checked the pressure to the gas valve which is actually 30mb!
The burner pressure is not givin a big reading approx 1mb although im not sure if this boiler has a zero govner, (i think not)
You think right!
What is the working pressure? (incoming supply with burner on)
What is the burner pressure? (the test point above the one you've just tested with burner on)
What is the low gas burner pressure set to? (pull off one of the black leads with burner on)
i will re check again today,
when i checked yesterday working pressure was about 30mb (top of the gauge)
The burner pressure was about 2mb (although the burner appears to be on full this however may not be the case)
I couldnt get the boiler to fire with one of the black leads off, should i remove it once the boiler has fired?
Your min/max gas settings are way out. Get a corgi in to set boiler gas pressures up.
If burner still does not go to max burn with hot tap on full, then
1. modureg is shot
2. P.C.B is shot (most likely)