Both 32A breakers connected to undersized cable. Same with the 50A breaker!
What you can't see is that there is no earthing conductor connecting the cut-out to the installation.
There is a connection to the gas pipe, though...
I came to this property last week. I found a light fitting removed by a neighbour in an attempt to put a new (Class I) fitting up. To his credit he had abandoned the job, but left the cpc-less rubber sticking out of the ceiling & no lights working. I made this safe. I also found an old Wylex box, with no bond to the water & an undersized one to the gas.
I recommended a rewire & came back yesterday to quote.
I found this CU in place of the Wylex. The rubber wiring I had made safe was dangling out of the ceiling. The dead side of the loop had chock blocks on it, as did the switch, but the live loop cable was bared ready for connection & dangling once more out of the hole in the ceiling. It was live.
I was perplexed so the customer gave the number of his "fully qualified" electrician.
He claims he made the lighting wiring safe.
He claims he was worried about the old Wylex fusebox. Remember this was the old Wylex fusebox that had an earth connection from the cut-out and fuse sizes correctly matched to the cables.
So he replaced the Wylex board "with RCD's" so "it would be safer."
When I pointed out they were not RCD's, he argued they were.
When I pointed out there was no main earth to the installation and that the earth connection was via the gas pipe, he claimed he knew that it was unsafe but, "I'm coming back tomorrow to sort it all out".
"What it needs," he said knowingly, "is all ripping out and starting again: I'm putting in a quote soon." He continued, "That unprotected clipped cable in the cellar is a nightmare & once that is all enclosed in trunking, I'll feel a lot better."
Righto, removing the main earth, declining to fit RCD protection, not bothering with upgrading gas PEB's or the water at all, fitting incorrectly sized MCB's & not testing at all is totally acceptable, but naked clipped cable in the cellar oh, no!
May the Lord help him.
I wonder which quote the customer will accept?