Ideal icos he24 boiler constant 'c' with banging noises

Following the steps now. Will keep you updated. Thank you
 
  • Thanks
Reactions: CBW
Sponsored Links
Looks like you have 3 motorised valves ,do you have zonal heating or underfloor heating ?
 
20231130_113723.jpg

It turned out to be this one which is live coming from the hot water motorised valve! Problematic motorised valve attached below.
20231130_113514.jpg
 
Sponsored Links
Replace the actuator.
That's brilliant @terryplumb. I have now put the two orange (central heating) wires back and left the one from faulty actuator out. Now the heating is working perfectly and going to stand by when demand is off. And showing '0' boiler status.
This is brilliant analysis and perfect steps. Can't thank you enough. You are a star @terryplumb.
 
When the room temperature is less than required, it triggers the pump, the motorised valve and the boiler to go ON. The boiler then keeps firing up and off depending on its internal thermostat. Is this right?

Stat triggers the valve, then valve, once in position, triggers pump and boiler.
 