Hi Folks!
Went to a house today to investigate a fault. I have to say that I was called away and have to return, so I have not investigated further yet, sorry!
It was two bedroom SES fittings, three 40W lamps on each. They are switched via one 1G1W switch.
The lady was complaining that on switch off, a slight glow was emitted from the lamps.
Initially, I could not replicate the fault.
However, upon leaving the lights on a few minutes, I found that upon switch off, instead of the voltage falling away to zero (or thereabouts), it dropped to 48V.
I found the longer the switch was left on, the longer the residual voltage lingered, up to a maximum of around 10 seconds.
Then I removed all lamps and switched off after a few minutes. The voltage remained at 244V.
With one 40W lamp in circuit, the switched-off voltaged was 213V.
So I dropped the fittings to disconnect the switchwire in order to bell it out.
Strangely, there was both a loop in and out and a switchwire at both light fittings.
The IR between L & Sw L at the switch position with switchwires disconnected at the ceiling position is 0.001Mohm.
I had to leave, so left the switchwires disconnected and I will return in a couple of weeks.
An odd one.
Obviously there is some damage or a short of some kind on the switchwire, but more than that I cannot guess.
Any thoughts so far??
Went to a house today to investigate a fault. I have to say that I was called away and have to return, so I have not investigated further yet, sorry!
It was two bedroom SES fittings, three 40W lamps on each. They are switched via one 1G1W switch.
The lady was complaining that on switch off, a slight glow was emitted from the lamps.
Initially, I could not replicate the fault.
However, upon leaving the lights on a few minutes, I found that upon switch off, instead of the voltage falling away to zero (or thereabouts), it dropped to 48V.
I found the longer the switch was left on, the longer the residual voltage lingered, up to a maximum of around 10 seconds.
Then I removed all lamps and switched off after a few minutes. The voltage remained at 244V.
With one 40W lamp in circuit, the switched-off voltaged was 213V.
So I dropped the fittings to disconnect the switchwire in order to bell it out.
Strangely, there was both a loop in and out and a switchwire at both light fittings.
The IR between L & Sw L at the switch position with switchwires disconnected at the ceiling position is 0.001Mohm.
I had to leave, so left the switchwires disconnected and I will return in a couple of weeks.
An odd one.
Obviously there is some damage or a short of some kind on the switchwire, but more than that I cannot guess.
Any thoughts so far??