Low h/w pressure at bath taps.Lack of ht. on CWST.
Would eliminating tank and feeding the cyl. direct from mains be a possible solution?
 
Sponsored Links
this is an ordinary copper cylinder?

will you be upset when it bursts?
 
Sponsored Links
Low h/w pressure at bath taps.Lack of ht. on CWST.
Would eliminating tank and feeding the cyl. direct from mains be a possible solution?

I hope your joking :LOL: :LOL: :LOL:

What you need is to change your taps for low pressure system type or fit a booster pump next to the cylinder!
 
I have seen it done , with the expansion pipe sealed off and bugger me do you know the cylinder had split causing a bit of a leak below.
Not a good idea to make your own unvented.
 