This could take a while, bear with me.
A couple of years ago I posted about tripping of my RCD, well I’ve spent the last 2 years trying to narrow it down, but need some more help.
It’s a split load board, with only lights on the non-RCD side.
I have turned off the garage MCB, still trips, turned off the cooker MCB still trips.
Had it tested by an electrician under the house warranty, it’s the PC. Well on my 2 week holiday just finished, I unplugged all the PC equipment, and guess what. The people who checked the house tell me – it tripped.
I noticed that with the washing machine and dishwasher on at the weekend, it tripped. So I have unplugged the washing machine, and it hasn’t tripped. Today washing machine and dishwasher on again, it tripped. However yesterday the washing machine was on by itself, no trip, although at the weekend, it did.
I have no sockets in the house at all, not on the RCD protected side, otherwise I would check appliances by plugging in elsewhere. I have also observed a bulb blowing tripping the RCD, although only a couple of times.
It seems from the testing that has been done that there is a build-up in earth leakage to the point that it trips, hence why the electrician stated it was the PC – the last thing plugged in that caused it.
Is there anything I can do to isolate these appliances? The cooker socket does not have a normal socket with it, so can’t use that. I can’t even tell at the moment what ring is causing the grief, there are 3 in my house, 1 for each storey.
I have a multimeter, so is there any tests I can do, as a DIY man. I am loathed to get an electrician in at the moment, as sometimes its days between trips, sometimes 5 mins, unless there are tests that would answer the question quickly, at small cost.
Should I replace the RCD?
Thanks for reading, and sensible suggestions please.
Gary
A couple of years ago I posted about tripping of my RCD, well I’ve spent the last 2 years trying to narrow it down, but need some more help.
It’s a split load board, with only lights on the non-RCD side.
I have turned off the garage MCB, still trips, turned off the cooker MCB still trips.
Had it tested by an electrician under the house warranty, it’s the PC. Well on my 2 week holiday just finished, I unplugged all the PC equipment, and guess what. The people who checked the house tell me – it tripped.
I noticed that with the washing machine and dishwasher on at the weekend, it tripped. So I have unplugged the washing machine, and it hasn’t tripped. Today washing machine and dishwasher on again, it tripped. However yesterday the washing machine was on by itself, no trip, although at the weekend, it did.
I have no sockets in the house at all, not on the RCD protected side, otherwise I would check appliances by plugging in elsewhere. I have also observed a bulb blowing tripping the RCD, although only a couple of times.
It seems from the testing that has been done that there is a build-up in earth leakage to the point that it trips, hence why the electrician stated it was the PC – the last thing plugged in that caused it.
Is there anything I can do to isolate these appliances? The cooker socket does not have a normal socket with it, so can’t use that. I can’t even tell at the moment what ring is causing the grief, there are 3 in my house, 1 for each storey.
I have a multimeter, so is there any tests I can do, as a DIY man. I am loathed to get an electrician in at the moment, as sometimes its days between trips, sometimes 5 mins, unless there are tests that would answer the question quickly, at small cost.
Should I replace the RCD?
Thanks for reading, and sensible suggestions please.
Gary