So, you are suggesting de-rating the 32 A ring to 20A? Because what you have proposed would do just that.
OK, putting regulations aside for now, if the load was concentrated near the CU, yes it would be de-rated, because it needs to be due to Ohm's law. However, for a distributed load, the rating would increase towards 40A.
Both the ring final circuit and double socket outlet as we know them are pretty naff designs in the first place.
The basic design assumption of a ring is that the load will be evenly distributed around the circuit, and a double socket is designed as a single outlet (rated at 13 Amps only), that just happens to have two holes in the front so you can shove two plugs into it.
Unfortunately, there is nothing to prevent plugging a fan heater and a hair dryer into a double gang socket - so it'll have to cope. If it not designed to cope there should be an indelible label saying so (or a separate 13A fuse) - but there isn't.
If you believe the circuit is not going to be used in a way that follows those assumptions, then a ring final with double socket outlets is not an appropriate circuit design to use.
A domestic ring final must surely be considered an uncontrolled installation because bozos in their own home are free to plug in what they will where they will.
If you still consider a ring as an appropriate design, how would seperate MCBs or seperate poles of an MCB for each leg of a ring enhance protection?
I'm glad you asked
Say the load is not distributed evenly but concentrated at one end, the current flows mostly through one leg so one cable can carry nearly the entire rated current of the MCB - not good. Having multiple linked MCBs will protect against this situation. On the other hand, if the load is evenly distributed, the total load can approach 40A before tripping (close to that an old 30A semi-enclosed fuse installation). The designer no longer has to consider load distributions as a safety factor.
The proportion of the current in each side of the ring is already fixed by the cable lengths (= resistance) each side of the load, and a 30 or 32 Amp OCPD is selected as adequate protection, given there are two parallel paths, it should operate before the CCC of the shortest path is exceeded, so a single pole MCB is all that's necessary.
Adequate - probably, usually, mostly - keep fingers crossed.
If your design features seperate MCBs, tripping one MCB would just shunt the full load to the second MCB, which would (or should) trip too. But with one MCB tripped, the circuit has sudenly become a much longer radial circuit, but still carrying the same load. Is that circuit going to comply with the circuit design criteria for a radial circuit carrying that load?
Good point. However, if the total length of the ring is no longer than a radial...
Then there is the matter of having a single point of isolation for the circuit...
etc...
etc...
Now THAT I can appreciate and it all makes sense - thank you. Hence the desire for this hypothetical quad-pole RCBO.