Strange one for me but I am sure more experiences people will know this situation.
Two purpose built flats about 70 or more years old.
Supply is looped from downstairs flat to upstairs flat.
Each flat has its own cut out fuse.
Pulling the DS fuse isolates both properties
cable from DS to US flat is old VIR which needs to be replaced
DNO are coming to sort out the fuse situation, but refuse to run new cable between the two cutouts saying its a private submain
(don't understand that, perhaps a DNO person on here could explain)
Its a simple run of about 5 meters straight up, so was going to use 25mm2 SWA.
I was just wondering about the best enclosure to terminate the SWA cable
I could put ther L/N into henley blocks, but that leaves the issue of terminating the SWA.
I guess the DNO could put the tails straight into the cut out, as is now, so no need for henley blocks. But how to terminate the cable
What is the neatest solution to this
Two purpose built flats about 70 or more years old.
Supply is looped from downstairs flat to upstairs flat.
Each flat has its own cut out fuse.
Pulling the DS fuse isolates both properties
cable from DS to US flat is old VIR which needs to be replaced
DNO are coming to sort out the fuse situation, but refuse to run new cable between the two cutouts saying its a private submain
(don't understand that, perhaps a DNO person on here could explain)
Its a simple run of about 5 meters straight up, so was going to use 25mm2 SWA.
I was just wondering about the best enclosure to terminate the SWA cable
I could put ther L/N into henley blocks, but that leaves the issue of terminating the SWA.
I guess the DNO could put the tails straight into the cut out, as is now, so no need for henley blocks. But how to terminate the cable
What is the neatest solution to this