One (full) rad not getting hot

Joined
8 Feb 2015
Messages
223
Reaction score
7
Country
United Kingdom
Hiya.

One of the Mother-in-Law's upstairs rad's isn't getting hot; have bled it. I therefore assume system is either unbalanced or not enough pressure.

Can't find the valve to introduce more water/pressure into the system.

Can anyone spot it here please!?

Cheers
 

Attachments

  • IMG_20201018_143454280.jpg
    IMG_20201018_143454280.jpg
    156.3 KB · Views: 64
  • IMG_20201018_143448739.jpg
    IMG_20201018_143448739.jpg
    198.4 KB · Views: 60
  • IMG_20201018_143444992.jpg
    IMG_20201018_143444992.jpg
    167.9 KB · Views: 66
  • IMG_20201018_143437987.jpg
    IMG_20201018_143437987.jpg
    219.3 KB · Views: 61
Sponsored Links
Looks like it's fed from a loft tank ( f&e) and not a sealed / pressurised system. Does rad give water out the bleed valve on the rad ?
Does it have a TRV ( thermostatic radiator valve ) ??
 
Agree re loft tank. Yes rad gives water out. No it doesn't have a TRV
 
Are both valves open on the rad ? If so turn all other rads off by their TRV ( if they have one ) or their wheel head valve . Don't touch their lockshields. Run heating and see if bedroom rad heats.
 
Sponsored Links
Yeah they're open. Did as you said, and it's started getting hotter
 
When it gets upto the full temperature that you would expect it to ,open the other radiators valve. Hopefully all will now work ok ,if bedroom rad goes cold the system will need to be balanced.
 