Hi all, hoping someone out there can help... Could I run a 4.4kw double oven of a dedicated 2.5 t+e ring main? Ie the only appliance off the ring main will be the oven? Any advice will be greatly received.
You could yes, if it's dedicated supply. Does not require to be ring final circuit, a radial would be better.
2.5mm t&e can carry a maximum of 27A (that is without any cable de-ratings). Your oven requires 20A protective device on full load.
So you should be okay.
Personally would use at least 4.00mm cable.