- Joined
- 27 Jan 2008
- Messages
- 23,705
- Reaction score
- 2,670
- Location
- Llanfair Caereinion, Nr Welshpool
- Country
As already said we tend to jump up or down by a factor of 3. Mainly as the RCD has to trip between half rated value and whole rated value.
So we see 10mA, 30mA, 100mA and 300mA in common use.
After 500mA most are designed for use by a skilled or instructed person and are not able to be accessed by a normal person.
There are three values listed in the regulations 30mA, 300mA and 500mA the latter is a special case but basically 30mA protects against a shock and 300mA against fire.
The other use is where the earth system is not good enough and the value is determined by calculation. In the main rule of thumb sorry should say historically we used 100mA where the earth was not good enough as being robust enough not to trip too easy and sensitive enough to ensure it did trip under fault conditions.
The 2008 regulations have changed that some what and now most items are protected by 30mA.
As already said where a cabin is protected by 30mA non time delayed, the distribution unit with 100mA time delayed type S, and the main distribution unit with a 1A at 1 minute unit. A worker who knocked a nail through the wall to hang his coat on and hit the cable tripped out all the devices even though in theory only the 30mA one should have tripped.
However where the fault is not so dramatic for example dust and damp build up then using a 10mA plug in unit could stop the rest of the system tripping.
I have a 10mA socket supplying my shed to avoid any faults likely tripping my whole house. The house has two RCD's both 30mA and it is not unknown for both to trip together. Likely spike caused when first one trips then trips the second although so quick it seems both trip together.
Also resetting one often trips the second one. But my trips are old fitted in 1990 and today the trips are better made and don't trip as easy with spikes.
I have also used RCD's for a completely different job. At work I used active RCD's on all our grind stones. Not to protect from fire or shock but so that in event of a power cut on the power returning the grind stones would not auto re-start. This with old lawn mowers without deadman's controls this may still be a good idea.
The higher quality RCD's give warning between 50% and 90% and only trip between 90% and 100% of rated value. There are even auto resetting RCD's.
As well as active and passive there are RCD's for sine wave only, some will work with square wave and very special types for DC.
All now work with current but back in the third quartile of 20th Century we had voltage types. Now these could not be run in tandem and so you may find old books telling you how only one ELCB can be used. That would now be called an ELCB-v and a RCD can also be called an ELCB-c.
As to name I do agree it could cause people to think you are a spark but you did to be fair declare you were not so not really a problem. One one forum the admin started putting pro against qualified people but this back fired when tradesmen answered questions away from their expertise. And on another site all posts were monitored before being published and again this back fired as the admin then took responsibility for being a correct answer. We all make mistakes and for anyone to take any of the information given on any forum as true without checking they are taking rather a high risk.
Remember I have not talked about the special RCD's used by skilled persons and there are so many slight variations that I am sure there are types I have never seen.
But using two standard 30mA RCD's on same circuit in tandem will not reduce the effectiveness of either.