plumbing and heating: wire a towerstat rf into my ideal isar

Discussion in 'Plumbing and Central Heating' started by alfieboy1, 17 Aug 2010.

  1. alfieboy1

    Joined:
    17 Aug 2010
    Messages:
    7
    Thanks Received:
    0
    Location:
    Essex
    Country:
    United Kingdom
    Hi I wonder if anyone can help im trying to wire a towerstat rf into my ideal isar HE 24 on the boiler wiring I have a 5 core cable BLU BROWN BLK GREY & EARTH THE BLK AND GREY are not connected and there is a link wire between the 2 terminals marked L1 & L2 the BROWN is wired into L3 Earth into Earth and BLU into N on the back of the stat I have a N & L & NO & NC and a COMM for 230v wiring it looks like you put a link between L & COMM N to N can anyone tell me what L1 and L2 are and in what order are they SL on or SL off as note to sure what gos where
    Regards Alfieboy1
     
  2. D_Hailsham

    Joined:
    18 Oct 2007
    Messages:
    9,212
    Thanks Received:
    1,117
    Location:
    Sussex
    Country:
    United Kingdom
    There are to ways you can wire this.

    1. Link L to Common at the Stat and connect NC (SL ON) to L2

    2. Connect Common to L1 and NC (SL ON) to L2

    In both cases, there must be a supply to L and N of the Stat; and the link must be removed between L1 and L2
     
  3. alfieboy1

    Joined:
    17 Aug 2010
    Messages:
    7
    Thanks Received:
    0
    Location:
    Essex
    Country:
    United Kingdom

    Hi thanks for promp reply so there is no need for the L1 to be used I did try it this way with just a switched live and got no heating when called for on stat got the fan blade symbol come up but no heating i did wire a honeywell stat between L1 and L2 and that works fine but that was only on a fly lead
    Regards Alfieboy1
     
  4. D_Hailsham

    Joined:
    18 Oct 2007
    Messages:
    9,212
    Thanks Received:
    1,117
    Location:
    Sussex
    Country:
    United Kingdom
    Have you checked that the two parts of the Towerstat talk to each other?

    First check the RF addresses are the same (page 7 - RF Address Code setting)), then check communication between the two parts (page 17 - testing RF transmission range).

    Do you have a multimeter? If so you can check the voltages.
     