Central heating system not working right.I have had british gas guy out rads down stairs not getting hot upstairs was shut them down bottom rads got warm but after period of time some went cold again ,also kettleing sound from boiler says its down to poor circulation due to pipes being blocked or restricted also on pipes near pump used a magnet on a stick which stuck to pipes and sys it needs power flushing does this sound right
 
Sponsored Links
Sounds right to me! About £350 at independent prices.

System dirt not normally covered in most BG contracts.

Tony
 
Agile said:
Sounds right to me! About £350 at independent prices.

System dirt not normally covered in most BG contracts.

Tony
there saying £520 but covered for life thats on four bed with twelve rads do you what magnet was about
 
Sponsored Links
"covered for life" will depend on keeeping the system filled up with inhibitor mixed in the water. Otherwise it will just corrode again.

For an extra £100 or so you could have a Magnaclean which will trap remaining sediment (yes, there will be some) that circulates in the water to stop it building up into another blockage or wearing the pump out.
 