No softus you don't increase the pressure
You store water at the static pressure which in turn boost the poor flow rate.
If you say store 50 litres at 1.5 bar, when you open a tap the mains pressure drops to say 0.75bar, the water stored in the accumulator will then top the flow volume up to it original say 17litres a min, until the vessel is depleted.
It is the reason why the accumulator has to be huge, and in most cases the gain is not worth the outlay.
Weight and space is a major problem in most houses as you need a room to fit it all in.
As I have said the higher the pressure you can store in the vessel the bigger the advantage if you release that pressure at a controlled rate, 4-1 Is the figure we try to get.
We have used accumulators for top-up vessels on heating systems where no mains has been available, pumping the water into the vessel with a hose pipe and pressure testing bucket, needs checking yearly and topping up as necessary.
And for the eggheads
who are quoting boyles law, he was talking about the air, not the water that compressing it, the more water you can get in the more water you can get out.