Potterton Suprima 30 boiler ignites and runs for about 5 mins then goes off. I get a red solid light and a green flashing light but the boiler then does nothing. Could the temp sender be faulty or the overheat stat need replacing ?
Can also be blocking fault which tec support say is that the incoming mains frequency is out of spec should be 50hz(more likely to be faulty pcb), as said check aps & fan then look at upgrading to new mk3 pcb, which is much more reliable and has better on board fault diagnosis
If you need to find a tradesperson to get your job done, please try our local search below,
or if you are doing it yourself you can find suppliers local to you.
Select the supplier or trade you require, enter your location to begin your search.
Please select a service and enter a location to continue...
Are you a trade or supplier? You can create your listing free at DIYnot Local