Pressure gauge not reading correct

Joined
22 Nov 2009
Messages
4
Reaction score
0
Country
United Kingdom
Have a Vokera boiler on a sealed system. the gauge on the boiler reads different than the gauge at the filling point (cylinder, upstairs). I currently have a leak which I am in the process of fixing and I need to top up regurily, if the boiler is at 1 bar and will not light then I top up to 2 bar at the hot water cylinder and the gauge there reacts straight away but the boiler gauge does not change, maybe 24hrs later it will have moved .2 of a bar. Is this gauge faulty?
 
Sponsored Links
When just topped up the gauge at the cylinder will be 2 bar while the boiler will be at 1 bar and will not move much (maybe .2) in 24 hrs
 
Sponsored Links
Pump can change the reading up to about .5, but usually no more than about .3.
Every meter vertical difference between the 2 accounts for 0.1
Neither gauge is calibrated so could easily be out 0.2 - 0.3 each
 