Problems with tepid shower water

Joined
21 Jan 2013
Messages
12
Reaction score
0
Location
London
Country
United Kingdom
Hi,

I have an Ariston EuroCombi boiler and Mira Excel B mixer shower.

I'm currently experiencing some oddities with the plumbing because when I turn on the shower, the water only ever gets warm and stays warm. However, when I turn on the bath hot water tap, leave it running, then turn on the shower the water is hot.

Any ideas or suggestions would be really welcome!

Kind regards

Ria
 
Sponsored Links
Turn off the heating and let the pipes cool, when the pipes are cool run the hot water and see if the central heating pipes start to get warm, post back what happens.
 
I have 5 pipes from the boiler - 3 'fat' and 2 'thin'.

When running the hot water one fat and one thin pipe get warm, the others remain cold.
 
The diverter valve in the boiler needs to be replaced, make sure whoever you get to do it confirms the diagnosis before pulling the boiler to bits.
 
Sponsored Links
OK great, thanks very much for your help. I will report back once sorted.
 
Just to update you, I had an engineer round to fix the boiler. It turns out it was the heat exchanger, it was full of black gunk. Now that it's been cleaned out it the shower is lovely and hot!

Thanks for all your replies.
 
Thanks for the feed back, glad to hear you got it sorted.
 