My 8.5Kw shower recently sprang a leak, the saddle connector for the water supply split. Any way whilst the front was off i took the oportunity to run some tests on it.
Its on 10mm cable to a 30ma RCD with isolators in between with a neon indicator. Its a TNCS supply
The R1+R2 reading came in at 1.06 and the Zs at 0.28.
If my notes are correct for a radial Zs= Ze + R1+R2 If i have a theoretical Ze of 0.35 the sums dont work.
Can any one help and as its well within limits does it matter.