Thanks thats all useful, having thought about it I too realised inrush must be a large part of the Henry causing trips. Its fairly new so I had no immediate reason to suspect a fault.
Only the one fridge freezer on the entire circuit - all other 'white' appliances on another DB entirely in another part of the house. I would estimate the remainder as being 1 PC, and plenty of tablelights etc.. 95% of which are 12V type fed by plug in transformers. All other loads are resistive.
A clamp on ammeter is something I dont own - but could easily borrow. It would help tie things up for sure.
One thing I have never understood is something I came accross a few years ago. A old fuseboard had everything via a 30mA RCD - no real reason as it was a modern flat with PME. It would trip, but when reset, usually last about 15 minutes before going again. I (finally) traced the fault to an overheated pendant - on the actual bulbholder itself. It had been fitted with a 150W bulb, and so the casing was scorched to the point of crumbling, but it was a modern type fed by 2 core flex only. The heat had turned the copper wires purple, and presumably as a result high resistance, as happens when some idiot uses 0.75mm flex to connect a 3kw fan heater!
I understand the 15 minutes being due to the bulb heating up, but how does a 2 core flex, with no path to earth (suspended by PVC flex in mid air!) cause a leakage trip, rather than an overcurrent? Forgive me if I have missed some fundamental of electrical circuits, but it has bugged me to this day!