RCD or not RCD

Joined
31 Mar 2006
Messages
84
Reaction score
0
Location
Yorkshire
Country
United Kingdom
Just started second fixing our new consumer unit, just want to check my plans regarding the split load configuration of the board.

This is what i plan, Does this sound right?

NON RCD SIDE

32A Cooker 6mm
20A Immersion Heater 4mm
16A Socket Radial (office ict equipment only) 2.5mm
16A Central Heating 2.5mm
16A Alarm System 2.5mm
6A Lights Down 1.5mm
6A Lights Up 1.5mm
6A Smoke Alarms (x5) 1.5mm

RCD

40A Shower 10mm
32A Sockets Down Ring 2.5mm
32A Sockets Up Ring 2.5mm
32A Sockets Garage Ring 2.5mm
32A Basement workshop small CU (via 6mm SWA)
6A Lights Garage 1.5mm
6A Outside Lights 1.5mm

Any comments?

Cheers, Adam
 
Sponsored Links
No need to put the garage & outside lights on the RCD side.

Where is the office located? IMHO the office radial should be on the RCD side.

I assume that you are installing this to BS7671 16th edition? And that you have notified the local authority before starting work?
 
The office is on the ground floor with normal ring sockets in the room. But the radial circuit refers to a length of dado trunking on the wall containing a number of power and data sockets.

Is their a reason why the garage lights and outside lights should not be on the rcd? I just thought that as they were outside it would be better.

I am working to 16th and LABC have been notified and first fix has been inspected.
 
No need to put the garage & outside lights on the RCD side.

Where is the office located? IMHO the office radial should be on the RCD side.

I assume that you are installing this to BS7671 16th edition? And that you have notified the local authority before starting work?
hi if you can take power from the garage to say a lawn mower
surely the garage should have RCD protection also the cable run from the house to the garage
 
Sponsored Links
Read his post.

Sockets Garage Ring
is on the RCD side.

Cables run from house to garage must have over current protection but not needed RCD protection for the cable itself.
You do need RCD protection for the application (eg sockets likely to be used to power portable equipment outdoors).

Edit: Reading between the lines I would guess the garage is attached to the house - may even have the consumer unit in there? Otherwise he would run a separate SWA feed to a detaached outbuilding..??
 
hi if you can take power from the garage to say a lawn mower
surely the garage should have RCD protection also the cable run from the house to the garage

Garage sockets are on the RCD side, he said that garage lights didn't need to be on the RCD side.
No need to RCD protect a cable from the house to the garage as long as RCD protection is made available in the garage for sockets.
 
No need to put the garage & outside lights on the RCD side.

Where is the office located? IMHO the office radial should be on the RCD side.

I assume that you are installing this to BS7671 16th edition? And that you have notified the local authority before starting work?
the GARAGE & outside lights
 
the GARAGE & outside lights

NON RCD SIDE

32A Cooker 6mm
20A Immersion Heater 4mm
16A Socket Radial (office ict equipment only) 2.5mm
16A Central Heating 2.5mm
16A Alarm System 2.5mm
6A Lights Down 1.5mm
6A Lights Up 1.5mm
6A Smoke Alarms (x5) 1.5mm

RCD

40A Shower 10mm
32A Sockets Down Ring 2.5mm
32A Sockets Up Ring 2.5mm
32A Sockets Garage Ring 2.5mm
32A Basement workshop small CU (via 6mm SWA)
6A Lights Garage 1.5mm
6A Outside Lights 1.5mm

Garage and outside lights ie garage lights and outside lights.
 
Garage lights and outside lights do not need to be on the RCD.

Thought it was implied by typing "garage and outside lights" but there ya go...
 
Does this sound ok then? Going to second fix it tomorrow.

NON RCD SIDE

32A Cooker 6mm
20A Immersion Heater 4mm
16A Central Heating 2.5mm
16A Alarm System 2.5mm
6A Lights Down 1.5mm
6A Lights Up 1.5mm
6A Lights Garage 1.5mm
6A Outside Lights 1.5mm
6A Smoke Alarms (x5) 1.5mm

RCD

40A Shower 10mm
32A Sockets Down Ring 2.5mm
32A Sockets Up Ring 2.5mm
32A Sockets Garage Ring 2.5mm
32A Basement workshop small CU (via 6mm SWA)
16A Socket Radial (office ict equipment only) 2.5mm
 