Replacing an MCB

Discussion in 'Electrics UK' started by jeffturl, 22 Mar 2012.

  1. jeffturl

    Joined:
    4 Jul 2009
    Messages:
    6
    Thanks Received:
    0
    Location:
    Devon
    Country:
    United Kingdom
    I am looking to replace the electric shower, the current one is a 8.5kW the new one will be 10.5kW. The current cabling from the shower to the consumer unit is 10mm (i checked before i bought the shower!). The MCB in the consumer unit is rated at 40A. I have picked up a 50A MCB from my local merchants.

    My question is about how to safely replace the MCB in the consumer unit. The consumer unit has an RCD switch that covers all MCBs, is it safe to flip the RCD to off and replace the existing 40A MCB with the 50A? or do i need a professional in to safely isolate the consumer unit to carry out this work?

    The main fuse before the consumer unit is rated at 80A.

    Regards
    Jeff
     
  2. scousespark

    Joined:
    18 Jan 2006
    Messages:
    732
    Thanks Received:
    41
    Location:
    Merseyside
    Country:
    United Kingdom
    The work has to be notified to your LABC.
    The safest option you have is to use a Part-P registered electrician.
    If you need to ask the questions you have asked, you shouldn't think about doing this yourself.
     
  3. plugwash

    Joined:
    28 Mar 2004
    Messages:
    8,818
    Thanks Received:
    265
    Country:
    United Kingdom
    It SHOULD be if the consumer unit is installed correctly.

    However since you don't know whether the consumer unit has been installed correctly you should take extreme care not to touch anything inside when first removing the cover and immediately after removing it you should check for any exposed metal on the incoming connections.

    It's borderline depending on exactly how narrowly the "replacing fixed equipment" exception is interpreted.
     
  4. Chri5

    Joined:
    19 Jan 2007
    Messages:
    4,118
    Thanks Received:
    369
    Location:
    London
    Country:
    United Kingdom
    The rcd off still means that there is power in to the cu. you should turn off the main switch and turn off the power between main head and cu if you have an in line isolation between the two items.

    The mcb should be tested, hence that tends to take the job on to a qualified spark. As for paperwork since the circuit is being upgraded rather than replaced like for like, a cert is required.
     
  5. riveralt

    Joined:
    4 Jan 2004
    Messages:
    4,018
    Thanks Received:
    596
    Country:
    United Kingdom
    Before you go changing anything have you read the manufacturers instructions regarding the size of the MCB required.
    Firstly, the 10.5kw shower will be the headline figure used to sell the product and will be calculated at 240v. The regulations use 230v as the standard figure thus giving the actual rating around 9.6kw. Check your instructions and you will see they give the standard equivalent figure as well.
    You have 10mm cable so there is no problem regarding the size of the cable though 6mm T&E would have done.
    The purpose of the MCB is to protect the cable and often the manufacturers will require a 40Amp MCB for this size shower.

    If they require a larger size MCB then you're back to notifying your Local Authority Building Control in which case it might be cheaper to employ an electriican as previously stated.

    As Chris5 said if you turn the RCD off (I assume it incorporates the main switch as well) then the inside of the Consumer will still be live in places and you need to be very careful, especially if the MCB is positioned next the the RCD.
    If there is a double pole isolator between the meter and the cu then turn it off here otherwise, be very careful.
     
  6. scousespark

    Joined:
    18 Jan 2006
    Messages:
    732
    Thanks Received:
    41
    Location:
    Merseyside
    Country:
    United Kingdom
    Granted notifiability is open to interpretation.

    However, there is no vagueness when it comes to advising the op to get an electricain in to sort this. I don't think I have ever seen an electrician give advice to open the CU up and 'be careful not to touch anything'.

    Have you ever heard of safe isolation?

    This was for the benfit of Plugwash.
     