I am going to rewire the shed and just wanted to make sure that I did it right.
At the moment the way it is wired up is 16amp MCB to 2.5mm T+E to Metal app box to 2.5mm SWA going through the wall of the house, then along the ground, into the shed, along the shed floor at the back of the shed, along the shed floor at the side of the shed, and into a metal ccu.
From the shed ccu:
goes to one double socket.
goes to a 2 Gang light switch, which runns: First Gang= Shed light. Second Gang= Floodlight on back of house to light up the garden.
The way I was going to rewire the shed was:
Change 16amp MCB for 32amp MCB
Change 2.5mm T+E for 4mm T+E
Keep the same metal app box
Change 2.5mm SWA for 4mm SWA and clip it up to the outside of the shed, and also clip it up inside the shed.
Put in a New ccu with MCBs in the Shed
Put in three double sockets, one near door, one at back of shed near workbench, one on other side of shed for Frezzer and Tumble Dryer, as a ring.
Keep the same 2 Gang lightswitch, but change shed light to a 4 ft Single Fluorescent tube, and keep Floodlight on outside of house (its a PIR Floodlight).
At the moment the way it is wired up is 16amp MCB to 2.5mm T+E to Metal app box to 2.5mm SWA going through the wall of the house, then along the ground, into the shed, along the shed floor at the back of the shed, along the shed floor at the side of the shed, and into a metal ccu.
From the shed ccu:
goes to one double socket.
goes to a 2 Gang light switch, which runns: First Gang= Shed light. Second Gang= Floodlight on back of house to light up the garden.
The way I was going to rewire the shed was:
Change 16amp MCB for 32amp MCB
Change 2.5mm T+E for 4mm T+E
Keep the same metal app box
Change 2.5mm SWA for 4mm SWA and clip it up to the outside of the shed, and also clip it up inside the shed.
Put in a New ccu with MCBs in the Shed
Put in three double sockets, one near door, one at back of shed near workbench, one on other side of shed for Frezzer and Tumble Dryer, as a ring.
Keep the same 2 Gang lightswitch, but change shed light to a 4 ft Single Fluorescent tube, and keep Floodlight on outside of house (its a PIR Floodlight).