on a pass time
Yes on a concrete padstone
Span is 2850mm
178x102x19 ub
Thanks
100mm is standard for steel beams.Your BCO may want to see some calcs for an 80mm bearing, 150 is standard.
The crushing strength of the average concrete padstone is around 50 N/mm²; when safety factors are taken into acount, this is reduced to around 20 N/mm².
If the beam is 102mm wide, and the bearing is 80mm, that gives a contact area of approximately 8,000 mm², so that the maximum load allowed on the padstone surface would be 20 x 8,000 N = approx 160 KN.
This is way, way above the load that will show in the SEs' calculations for the beam; it is not a problem.
There are other factors to be taken into account when using a short bearing, but in practice they would not apply in a domestic situation where the loads are relatively low.