It's a 23A load using the conventional diversity calculation.2 ovens, microwave,& steam oven on a 32a RCBO ? mm, that's a pain in the ass when it trips !
How/when/why would that trip a 32A breaker?
It's a 23A load using the conventional diversity calculation.2 ovens, microwave,& steam oven on a 32a RCBO ? mm, that's a pain in the ass when it trips !
I suspect DS was thinking of the inconvenience (and possible difficulties in fault finding) if one lost all one's cooking appliances as a result of a L-E or N-E fault in one of them causing the single RCBO to operate. As I wrote, I might possibly split the appliances onto two RCBOs for that reason - but, even if I did that, I would still add them all together and apply diversity to the total for the purpose of determining the load on the installation.It's a 23A load using the conventional diversity calculation. How/when/why would that trip a 32A breaker?2 ovens, microwave,& steam oven on a 32a RCBO ? mm, that's a pain in the ass when it trips !
So in a professional capacity would you always advise people to never buy anything like this:It's an RCBO ………….
DS
There's always Plan B: Don't use an RCD device on that circuit.I suspect DS was thinking of the inconvenience (and possible difficulties in fault finding) if one lost all one's cooking appliances as a result of a L-E or N-E fault in one of them causing the single RCBO to operate. As I wrote, I might possibly split the appliances onto two RCBOs for that reason
There is, but (even if one feels that RCD protection is not necessary for 'safety' reasons) that will quite often introduce hassles in terms of the wiring of the circuit.There's always Plan B: Don't use an RCD device on that circuit.
Kitchen cooking appliances 32A
2 ovens, microwave & steam oven
Induction Hob 32A
Other kitchen & utility sockets / appliances 32A
Socket outlets & other fixed items
20A for basement
20A for ground floor
20A for first floor
20A for loft
Lighting
6A lights basement & first floor
6A lights ground floor & loft
12 way main switch CU with 9 RCBOs for the circuits above and 3 spaces for any future items.
Judging by the kitchen money is not an issue.
Judgement ?
So in a professional capacity would you always advise people to never buy anything like this:It's an RCBO ………….
DS
Judgement ?
Yep, you said "judging by" so I took that to be a judgement.
I am afraid for some reason there aren't many second hand 17th edition amendment 3 CUs around at the moment, otherwise I would [/QUOTE
i have just bought a Hager 10way for £50.00 on ebay he had two for sale.
DS
It's suggested somewhere, but not required.That makes very good common sense, although don't smoke alarms need to be on their own circuit? Or is that just recommended and not required?
Having a dig at me by saying "Don't tell Ban that we're advising putting a 100A+ load onto a 100A fuse......" even though that would have been completely untrue, and all because I'd said one should not put a 26A load on a 20A breaker.What is?
No it isn't suggested. BS 5839-6 (which covers domestic detection) actually states a preference for the lighting circuit so as they are not left de-energised.It's suggested somewhere, but not required.That makes very good common sense, although don't smoke alarms need to be on their own circuit? Or is that just recommended and not required?
Connected to a lighting circuit is fine, and also means people notice quickly if the circuit is off for any reason.