just trying to get some input off a few more people. i called round to a property yesterday to replace a faulty socket. when i went to isolate the circuit i found that the down stairs sockets were on 2 2.5mm 16A radials. i noticed that the kitchen and all the appliances were supplied via 1 radial and the living room was supplied via the other. i spoke to the customer about the loading on the kitchen radial and he told me that the sockets use to be on a ring. apparently an electrician (who used to work at my work) had called round a couple of years ago and found a fault on the ring. instead of renewing the damaged cable this sparky decided to disconnect the cable and turn into two radials. i know that this is safe but i am unimpressed with the possible load on the kitchen radial (2.5mm 16A 60898) as 2 appliances could overload the circuit. spoke to one of the lads at work who told me this is ok and to just leave it. i spoke to my boss and we decided that i will come back and renew the damaged cable and turn back into a 2.5mm 32A ring.
so just wondering what other peoples take in this situation would be. i.e break a ring that was designed and installed by some one else with regards to load and turn into radials. or replace damaged cable and keep the ring as designed?