Hi All
First things first, I intend getting an electrician in to connect cable to consumer unit which is 100a but would appreciate your thoughts on me doing all of the donkey work first, any corrections or criticisms truly appreciated.
8.5kw shower, above bath, back of airing cupboard.
10mm cable from shower into airing cupboard running in mini trunking for 1.5 metres then into loft space.
Can I cable clip to joist or trunk for further 2 metres, not near insulation or metallic objects.
Drop down into 45 amp double pole isolation switch, ceiling mounted, carry on up through loft for a further 2 metres, then drop through ceiling down into mini trunking for 7 metres, through wooden floor board (now into consumer unit cupboard) to a 63 Amp 30ma RCD, then to a 40 amp separate MCB.
Thoughts?
Regards all