The picture that follows is quite unremarkable - the story is not!!
Went to this today - complaint of shower not working. Looked at Shower - 8.5kW - 37A was running off 30A 3036.
Thought it was a case of an overload plus maybe a loose connection.
Told the customer the bad news. Her reply was "Which shower have you looked at?"
When I said, "the one in the main bathroom", she replied, "No, the one I want you to look at is in the ensuite..."
Turns out there are 2 showers on this feed,
8.5kW & 9.5kW. 78.3A....
No wonder it failed....!!