Did he design it himself, in a position of ignorance, or did he employ an architect? If the latter I think he's been the victim of negligence...CathalX said:In answer to the question "why so much heating", the house was designed in a very 'money no object manner'. He wanted under floor heating in each room downstairs but because the rooms are so large, three to five elements were needed in each. He didn't really consider the supply implications or running costs.
FWL_Engineer said:Cathal, I think your also labouring under a false premise, have you forgotten DIVERSITY??
Yes you have
170A Potential Heating load
6kW Potential Lighting Load
3 Rings with a potential loading of 96A MAXIMUM
In reality, due to occupancy and the way people use a home, you will have likely loadings of
60A Heating
9A Lighting
40A maximum across all three rings
Giving a grand total of 109A which would require a 30kVa supply to give an upper cieling.
The heating elements will be Thermostatically and Timer controlled, so it is highly unlikely that all will be on at the same time, if the house is as well insulated as you imply then they are likely to be on only intermittently.
I would simply recommend that the supply be uprated from 16kVa to 30kVa.