Hi all, just hoping someone could point me in the right direction as my boiler is doing (what I think) some strange things.
Potterton Suprima 50L - looks like it had a new board fitted a few years ago (5102160) so I'm hoping it's not that.
It constantly cycles:
Orange/Green light flashes for a few seconds
Fan turns on
Ignitor starts
Lights ok
Green Light goes constant
Cover starts to bang and what sounds like air blowing out in pulses(?) (5-10 seconds)
Shuts off and light goes Orange
Light goes back to Orange/Green flashing
Repeat
It can get very windy here and I've noticed on a particulalry bad day the boiler won't run for longer than about 15-20 secs before cycling. However on a calm day it'll run ok (plenty of hot water, heating etc.) BUT only if I unscrew the front cover a few mm to 'relieve the pressure' (the banging is greatly reduced) - I know this is not advisable but I'm just trying out different things. Obviously when the wind gets up again, the smell gets pretty bad so I tighten it up but then it shuts off.
I tested the pressure switch and it seemed ok. I then had a British Gas inspection done (the one where they come and look over the system before you take one of those contracts out) he said before they could proceed the pressure switch is faulty and needs replacing - other than that everything else seemed ok. He quoted £120 for the switch & fitting. I asked what else it could be if it wasn't the switch and was told it couldn't really be anything else.
I bought a replacement Honeywell from boilersparesuk, fitted it and still get exactly the same problem! Is it likely that the switch is faulty or could it be something else? For example the flue outlet is on the front of the house about 5-6m horizontally from the boiler (like I say it can get windy here), just opening the cupboard door which houses the boiler you can hear the wind blowing down the hole for the flue...could this be some of the cause?
Thanks guys, sorry for the long post, I thought the more info I supply the better!
Potterton Suprima 50L - looks like it had a new board fitted a few years ago (5102160) so I'm hoping it's not that.
It constantly cycles:
Orange/Green light flashes for a few seconds
Fan turns on
Ignitor starts
Lights ok
Green Light goes constant
Cover starts to bang and what sounds like air blowing out in pulses(?) (5-10 seconds)
Shuts off and light goes Orange
Light goes back to Orange/Green flashing
Repeat
It can get very windy here and I've noticed on a particulalry bad day the boiler won't run for longer than about 15-20 secs before cycling. However on a calm day it'll run ok (plenty of hot water, heating etc.) BUT only if I unscrew the front cover a few mm to 'relieve the pressure' (the banging is greatly reduced) - I know this is not advisable but I'm just trying out different things. Obviously when the wind gets up again, the smell gets pretty bad so I tighten it up but then it shuts off.
I tested the pressure switch and it seemed ok. I then had a British Gas inspection done (the one where they come and look over the system before you take one of those contracts out) he said before they could proceed the pressure switch is faulty and needs replacing - other than that everything else seemed ok. He quoted £120 for the switch & fitting. I asked what else it could be if it wasn't the switch and was told it couldn't really be anything else.
I bought a replacement Honeywell from boilersparesuk, fitted it and still get exactly the same problem! Is it likely that the switch is faulty or could it be something else? For example the flue outlet is on the front of the house about 5-6m horizontally from the boiler (like I say it can get windy here), just opening the cupboard door which houses the boiler you can hear the wind blowing down the hole for the flue...could this be some of the cause?
Thanks guys, sorry for the long post, I thought the more info I supply the better!